Can motor ground currents be generated by a 2-phase controlled softstart

Can motor ground currents be generated by a 2-phase controlled soft start, similar to common mode voltage/current generated by a PWM vfd?
06-01-2013 01:51 PM
Top #2
Mike
06-01-2013 01:51 PM
Never seen any common mode voltage problems caused by soft starters, but plenty from VFDs
06-01-2013 06:52 PM
Top #3
Rich
06-01-2013 06:52 PM
Our customer has a system powered by a generator, running a few fairly large (50, 60, 75HP) motors. They are using 2-phase softstarts with bypass and are seeing 20-30% imbalance on phases during start, along with almost 6 amps ground current. Once the bypass kicks in, all problems go away.
I have also discovered some ground loop issues, which may be contributing to this problem.
06-02-2013 07:53 AM
Top #4
Thusy
06-02-2013 07:53 AM
From experience - yes if no bypass contractor is fitted on the soft starter - leads to bearing pitting, thinning grease and ultimate bearing failure - solution insulate one motor bearing housing - normally NDE or fiit insulated bearing - additional fiit one earthing brush to shaft