For a 3.73 MW motor I got some budgetary quotations to put in a
variable frequency drive a year ago. These number may be different today but here they are:
$530,000 - 1 each medium voltage variable frequency drive 3.73 MW
$50,000 - 1 each medium voltage cable re-route
$50,000 - 1 each motorized motor disconnect switch between new drive and motor.
$5,000 - 1 each shipping of the new drive
$30,000 - 1 each auxiliary power feed equipment, MCC buckets, combinational starters etc.
$265,000 - 1 each enclosure for VFD for control air space includeing HVAC equipment.
$5,000 - 1 each shipping of enclosure
$250,000 - Installation labor contract for one (1) each drive
$20,000 - Engineering Design
$15,000 - Power feeds to the new enclosure for HVAC and control power and such
$5,000 - Lighting power feeds to new enclosure
$25,000 - Control wiring and modiciactions and tuning during startup, if synchronous motor you will might need an encoder on the motor shaft with cables and proximity switches between the drive and the motor.
$1,250,000 is the total Sum.
$1,625,000 is the total Sum times 1.3 (30 percent contingency factor).