Here is the way to set it:
Regarding the pressure set point issue, please refer to parameter P7.02 and P7.14 of the user manual for pressure setting. For example, if the measure range of your pressure
sensor is 10kg, and you wanna set 4kg as the feedback point, you just need to set P7.02 to 40.
The
variable frequency drive can provide DC 24V and 12V (Terminal 10V max voltage when open is 12V) for the pressure sensor, but can not provide 15V. Maybe you can use 12V for your pressure sensor.
Hope it helps