we want to run 3 compressor each 15 H.P on single VFD

we have pvc pipe plant due to low voltage and low connected load we want to use 15 HP 3 compressor on single vfd. compressor will never stop and start we have max 10 kg pressure cut off for com but from 9kg pressure we reduce rpm of com and when it reach to 6 rpm incrise
01-02-2014 12:58 AM
Top #2
Nitin Jhanwar .
01-02-2014 12:58 AM
Are you going to start all the compressor altogether. If yes get VFD at least 50 HP and connect all compressor together otherwise it is not possible to drive compressor with only one vfd. I am considering 3 phase motor.
01-02-2014 03:01 AM
Top #3
suresh khake
01-02-2014 03:01 AM
thank we are using 3 phase motor on lg compressor all run at a time. which vfd i sgood in terms of cost ,after sales service, spare part.we are base at dehradun haridawar.we have vfd on pvc extruder yaskkawa japan and vacon finland
01-02-2014 05:53 AM
Top #4
LIJO CHERIAN
01-02-2014 05:53 AM
Go for Siemens vfd.. They might be costly but serves well.and service its also good.
01-02-2014 08:30 AM
Top #5
Mohamed Said A.
01-02-2014 08:30 AM
maybe you'll have to connect a filter between your VFD and motors. This is described in the datasheet of the VFD.
Danfoss or Siemens are the best
01-02-2014 04:18 PM
Top #6
amit Das
01-02-2014 04:18 PM
In a machine i need to do oscillation.Using micromaster420 should i do?I have planed to use limit switch and reversing the motor rotation when i get feed back from LS.I have doubt that the frequency of oscillation should be very less.any one should any idea about this.
01-02-2014 07:15 PM
Top #7
Ramūnas Labonas
01-02-2014 07:15 PM
We made a big transporter system with 12 motors and have had big problems with heating of motors protections.
01-02-2014 09:57 PM
Top #8
Sevaganahalli Sreenivas Sateesh
01-02-2014 09:57 PM
Dear Amit das

try a servo motor for oscillation ,it is the best
01-03-2014 12:12 AM
Top #9
Sevaganahalli Sreenivas Sateesh
01-03-2014 12:12 AM
Dear Suresh

always find out the load current of the output and then decide since VFD is selected based on Load Current