Forum » General Discussion » What should be there %age with respect to FL I or rated I?
Topics: What should be there %age with respect to FL I or rated I? on General Discussion
#1
Start by
Kashif Amin
10-08-2013 09:41 AM

What should be there %age with respect to FL I or rated I?

Different protection devices eg fuse thermal overload CB & other equipment like magnet contactors are selected as certain %age of FL current. What should be there %age with respect to FL I or rated I?
10-08-2013 12:14 PM
Top #2
Lester Philip Lualhati
10-08-2013 12:14 PM
it depends upon your load specifications (phase, type of load, etc.):

in circuit breakers, instantaneous trip: 200-800% of FL current while inverse trip: 150-250% of FL current...
in thermal OL relays, 115-125% of nameplate current rating...
in fuse, for time-delay: 150-300% of FL current, whereas, non-time delay: 150-175% of FL current...
10-08-2013 02:41 PM
Top #3
Radhakrishnan Ranjan
10-08-2013 02:41 PM
If you are looking for High Voltage fuse application, you must refer to IEEE C37 Series of standards and there are UL standards of applications for Low Voltage fuses. They deal with specific application for each equipment.